This announcement is final follow up to the power outage from March 28,
2008.
The UPS manufacturer was here on April 10th and did some analysis of the
UPS to see if there was any information to be learned. The results show
that the UPS is functioning properly and is not overloaded and hasn't given
us any indication as to why the breaker tripped.
That leaves the breaker as the only possible source of this outage.
Further investigation of the breaker that tripped shows a high temperature
condition on the load side of the breaker. The line side is running at
normal temp. The electrician specifically indicated that this was not an
overtemp condition, but is a point of concern. This high temp condition is
likely caused by faulty or loose terminal connections into the breaker.
There are two possible paths for us to take to rectify this situation:
1. Attempt a hot fix by tightening the terminal connectors on the breaker
while under load. This is risky and does not guarantee the problem will be
solved. The only benefit of doing this hot fix is that we prevent a
scheduled downtime. The dangers of doing this hot fix is that tightening
the connections may cause the breaker to trip, CAUSING an unscheduled
downtime. Even if the tightening is successful, this would also leave the
old breaker in place. While the breaker is performing to specification
right now, it remains a questionable component within the entire system. I
do not prefer this method.
2. Schedule a downtime and replace the breaker with a new unit. This is
much less risky and will nearly guarantee the problem is resolved.
However, it does cause a scheduled downtime and requires everything
connected to the attached PDU be shut down in an orderly fashion. This is
the preferred method for two reasons, first, we are eliminating the
questionable element in the system and second, we are not risking an
unscheduled downtime from an accidental failure.
After weighing these options I have decided to replace the breaker and
schedule a system shutdown on Friday May 2, 2008 from 11:45pm until 1:00 am
central time. As this is major outage, this announcement is going out to
both our outages list and general announcements list. Please watch for
further announcements later today. If your cabinet is scheduled to lose
power during this downtime, you will be receiving an additional
announcement directly notifying you of the scheduled outage.
If you have any questions or want to know if you will be affected by this
scheduled downtime, please reply to this message and our support team will
inform you of your status.