Print

Print


On Sep 28, 2011, at 2:48 PM, Hannigan, Martin wrote:

> On 9/28/11 5:45 PM, "Jay Hanke" <[log in to unmask]> wrote:
> 
>>> 20P plugs are one horizontal and one vertical. If they have two vertical
>>> prongs, then
>>> they are NEMA 5-15P plugs which are much more likely on servers that are not
>>> drawing very high amperages.
>> 
>> The servers are all 5-15P. The outlet above the rack is a 20A twist
>> lock so we'll need an adapter.
>> 
>> Jay
>> 
> 
> 
> Folks,
> 
> We'd prefer that none of our equipment be modified without consultation of
> our deployment engineer responsible for this deployment. I'm sure that we'll
> be able to accommodate whatever environment that we need to and rapidly.
> 
> Best,
> 
> -M<

I don't think anyone said anything about modifying your equipment, Marty.

Ideally, the PDUs that provide the NEMA 5-20R or 5-15R receptacles in the
rack should have the NEMA L5-20P on their input cord.

Then, all that remains is to make sure that the total load being connected
to each PDU does not exceed 18A max or 15A continuous. (You should
always run a circuit with 25% continuous headroom and 10% max draw
headroom in order to allow for line losses, etc.).

Owen

########################################################################

To unsubscribe from the MICE-DISCUSS list, click the following link:
http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1