Building diversity.  Having all of our eggs in one basket is just asking for trouble.  

We were affected as well, but thankfully we have battery in our cage and were able to run until Cologix was able to amend the issue.  I haven't requested the RFO from them yet but will be doing so shortly.

Thanks,

Dean


-----Original Message-----
From: MICE Discuss <[log in to unmask]> On Behalf Of Frank Bulk
Sent: Monday, April 12, 2021 9:13 AM
To: [log in to unmask]
Subject: Re: [MICE-DISCUSS] MICE Issues

That's unfortunate!  Since this could easily happen again, what could be done to troubleshoot and/or mitigate the issue?

Frank 

-----Original Message-----
From: MICE Discuss <[log in to unmask]> On Behalf Of Jeremy Lumby
Sent: Sunday, April 11, 2021 8:25 AM
To: [log in to unmask]
Subject: Re: [MICE-DISCUSS] MICE Issues

When half of the power was taken down for maintenance, it caused a surge on the remaining side that tripped the breaker even though the circuit runs at less than 80% under failure conditions.  The breaker has been reset, and things are coming back online.  

-----Original Message-----
From: MICE Discuss [mailto:[log in to unmask]] On Behalf Of Jay Hanke
Sent: Sunday, April 11, 2021 8:00 AM
To: [log in to unmask]
Subject: [MICE-DISCUSS] MICE Issues

Cologix has done power maintenance in Suite 100 that has inadvertently affected the MN VoIP remote switch as well as most of the MICE monitoring.

This has isolated the SFN Remote Switch in Albert Lea. Cologix is investigating. No ETTR yet.

--
Jay Hanke, President
South Front Networks
[log in to unmask]
Phone  612-204-0000