Possibly.  I have only ever used them for devices that have only one power supply.  All of the impacted equipment had 2 supplies.  I think breaker tripping below it's rating is the biggest issue.  One of the Cologix techs mentioned to me that since the power strip was on the back (hot) side of the rack, the increased temp might have allowed it to trip easier than expected.

-----Original Message-----
From: MICE Discuss [mailto:[log in to unmask]] On Behalf Of Frank Bulk
Sent: Monday, April 12, 2021 3:31 PM
To: [log in to unmask]
Subject: Re: [MICE-DISCUSS] MICE Issues

Would an ATS that was between the power strips and each piece of gear have helped?
https://www.wti.com/collections/power-transfer-switch
We use them quite successfully. 

Frank 

-----Original Message-----
From: MICE Discuss <[log in to unmask]> On Behalf Of Jeremy Lumby
Sent: Monday, April 12, 2021 9:24 AM
To: [log in to unmask]
Subject: Re: [MICE-DISCUSS] MICE Issues

The powerstrip that had the breaker trip is being replaced with one that is slower acting to last through the surge that happens when all power transferred from the B to the A side.  I also agree with Dean that we need to diversify MICE some more.

-----Original Message-----
From: MICE Discuss [mailto:[log in to unmask]] On Behalf Of Frank Bulk
Sent: Monday, April 12, 2021 9:13 AM
To: [log in to unmask]
Subject: Re: [MICE-DISCUSS] MICE Issues

That's unfortunate!  Since this could easily happen again, what could be done to troubleshoot and/or mitigate the issue?

Frank 

-----Original Message-----
From: MICE Discuss <[log in to unmask]> On Behalf Of Jeremy Lumby
Sent: Sunday, April 11, 2021 8:25 AM
To: [log in to unmask]
Subject: Re: [MICE-DISCUSS] MICE Issues

When half of the power was taken down for maintenance, it caused a surge on the remaining side that tripped the breaker even though the circuit runs at less than 80% under failure conditions.  The breaker has been reset, and things are coming back online.  

-----Original Message-----
From: MICE Discuss [mailto:[log in to unmask]] On Behalf Of Jay Hanke
Sent: Sunday, April 11, 2021 8:00 AM
To: [log in to unmask]
Subject: [MICE-DISCUSS] MICE Issues

Cologix has done power maintenance in Suite 100 that has inadvertently
affected the MN VoIP remote switch as well as most of the MICE
monitoring.

This has isolated the SFN Remote Switch in Albert Lea. Cologix is
investigating. No ETTR yet.

-- 
Jay Hanke, President
South Front Networks
[log in to unmask]
Phone  612-204-0000